Devices > Remote Devices > Allen Bradley CIP EIE > Creating SLC-503/4/5 Custom Data Groups

Creating SLC-503/4/5 Custom Data Groups

Data groups for an SLC-503/4/5 controller (CIP_Protocol="PCCC_SLC") must be defined on a case-by-case basis.

You must create data groups that satisfy the following requirements:

An SLC data group enables you to access a file and its constituent elements. It requires that each XML data group element is mapped to a data file type and address component (that is, element, subelement, bit, and/or other component). Define data groups that map to address components and represent only those data items on an associated Allen-Bradley device that you want to include in your CygNet SCADA system. Addresses should be supplied by a PLC programmer or collected from the PLC program.

Your device template file provides a high degree of flexibility in defining SLC data groups. In a data group element, the elemAddr attribute enables you to specify the components needed to access virtually any data item on an associated SLC-503/4/5 controller. The syntax of the elemAddr attribute value follows the SLC standard, including the various Allen-Bradley SLC-503/4/5 delimiters.

For more information, see the following subsections:

For more information about SLCs, see the Rockwell Automation document SLC 500 Instruction Set Reference Manual (1747-rm001_-en-p.pdf).

To Create a Custom Data Group for SLC

  1. Using a text editor of your choice (but not Notepad), open a new or existing device template file where CIP_Protocol="PCCC_SLC" is defined.
  2. Define a data group element, including a data group name and description.
    1. Define a dgElements element.
    2. Define data group elements to meet your needs.
      • Each must be uniquely named.
      • Each must map to a data item on the associated field device by correctly defining an elemAddr and type attribute.
      • Each must use the correct Allen-Bradley file numbers and types as well as the correct syntax. See syntax sections below.
    3. Save your edits.
  3. When you are done editing the template, use the CygNet Device Template Manager utility (DtfMgr.exe) to check your work, then load the template to the applicable Device Definition Service (DDS), and test it by reading and/or writing values.

Note: The requests for non-contiguous elements are optimized to perform the fewest number of transactions for the device.

Example

Back to top

File Type Values

The following table provides addressing values to be used when defining CygNet SCADA data groups that are mapped to SLC data files.

File Type # Abbrev. Name Notes

0

O

Output

This file stores the state of the output terminals for the controller.

1

I

Input

This file stores the status of the input terminals for the controller.

2

S

Status

This file stores controller operation information. This file is useful for troubleshooting controller and program operation.

3

B

Binary, Bit

This file is used for internal relay logic storage.

4

T

Timer

This file stores the timer accumulator and preset values and status bits.

5

C

Counter

This file stores the counter accumulator and preset values and the status bits.

6

R

Control

This file stores the length, pointer position, and status bits for specific instructions such as shift registers and sequencers.

7

N

Integer

This file is used to store numeric values or bit information.

8

F

Float

This file stores single precision non-extended 32-bit numbers.

-

A

ASCII

This file stores 2 byte ASCII values. Can be file type 9 - 255.

-

ST

String

This file stores 82 byte string values. Can be file type 9 - 255.

9 - 255

N/A

N/A

Can be any file type except I or O.

Back to top

Output Data File and Input Data File (O0: and I1:) Syntax

The following table provides addressing formats and examples to be used when defining CygNet SCADA data groups that are mapped to SLC data files.

Format Parts Description

O:e.s/b

I:e.s/b

O

Output

I

Input

:

Element delimiter

e

Slot number (decimal)

.

Word delimiter

s

Word number

/

Bit delimiter

b

Terminal number

O:3/15

O:5/0

O:10/11

I:7/8

I:2.1/3

O:5

O:5.1

I:8

Output 15, slot 3

Output 0, slot 5

Output 11, slot 10

Input 8, slot 7

Input 3, slot 2, word 1

Output word 0, slot 5

Output word 1, slot 5

Input word 0, slot 8

Back to top

Status File (S2:) Syntax

The following table provides addressing formats and examples to be used when defining CygNet SCADA data groups that are mapped to SLC data files.

Format Parts Description

S:e/b

S

Status file

:

Element delimiter

e

Element number

/

Bit delimiter

b

Bit number

S:1/15

S:3

Element 1, bit 15

Element 3

Back to top

Bit Data File (B3:) Syntax

The following table provides addressing formats and examples to be used when defining CygNet SCADA data groups that are mapped to SLC data files.

Format Parts Description

Bf:e/b

Bf/b

B

Bit file

f

File number

:

Element delimiter

e

Element number

/

Bit delimiter

b

Bit number

B3:3/14

B3:252/00

B3:9

B3/62

B3/4032

Bit 14, element 3

Bit 0, element 252

Element 9

Bit 62

Bit 4032

Note: If a user is sending individual bits via a UIS command, not all bits are required to be defined as data group elements. If a user is sending individual bits via the data group editor, all bits should be defined as data group elements. Sending via the data group editor sends complete bytes and any bits not defined as data group elements are set to 0.

Back to top

Timer Data File (T4:) Syntax

The following table provides addressing formats and examples to be used when defining CygNet SCADA data groups that are mapped to SLC data files.

Format Parts Description

Tf:e.s/b

T

Timer file

f

File number

:

Element delimiter

e

Element number

.

Word delimiter

s

Word number

/

Bit delimiter

b

Bit number

T4:0/15 or T4:0/EN

T4:0/14 or T4:0/TT

T4:0/13 or T4:0/DN

T4:0.1 or T4:0.PRE

T4:0.2 or T4:0.ACC

T4:0.1/0 or T4:0.PRE/0

T4:0.2/0 or T4:0.ACC/0

Enable bit

Timer timing bit

Done bit

Preset value of the timer

Accumulated value of the timer

Bit 0 of the preset value

Bit 0 of the accumulated value

Back to top

Counter Data File Elements (C5:) Syntax

The following table provides addressing formats and examples to be used when defining CygNet SCADA data groups that are mapped to SLC data files.

Format Parts Description

Cf:e.s/b

C

Counter file

f

File number

:

Element delimiter

e

Element number

.

Word delimiter

s

Word element

/

Bit delimiter

b

Bit number

C5:0/15 or C5:0/CU

C5:0/14 or C5:0/CD

C5:0/13 or C5:0/DN

C5:0/12 or C5:0/OV

C5:0/11 or C5:0/UN

C5:0/10 or C5:0/UA

C5:0.1 or C5:0.PRE

C5:0.2 or C5:0.ACC

C5:0.1/0 or C5:0.PRE/0

C5:0.2/0 or C5:0.ACC/0

Count up enable bit

Count down enable bit

Done bit

Overflow bit

Underflow bit

Update accum. bit (use with HSC in fixed controller only)

Preset value of the counter

Accumulated value of the counter

Bit 0 of the preset value

Bit 0 of the accumulated value

Back to top

Control Data File (R6:) Syntax

The following table provides addressing formats and examples to be used when defining CygNet SCADA data groups that are mapped to SLC data files.

Format Parts Description

Rf:e

Rf:e.s/b

R

Control file

f

File number

:

Element delimiter

e

Element number

.

Word delimiter

s

Word element

/

Bit delimiter

b

Bit number

R6:2

R6:2/15 or R6:2/EN

R6:2/14 or R6:2/EU

R6:2/13 or R6:2/DN

R6:2/12 or R6:2/EM

R6:2/11 or R6:2/ER

R6:2/10 or R6:2/UL

R6:2/9 or R6:2/IN

R6:2/8 or R6:2/FD

R6:2.1 or R6:2.LEN

R6:2.2 or R6:2.POS

R6:2.1/0

R6:2.2/0

Element 2, control file 6

Enable bit

Unload Enable bit

Done bit

Stack Empty bit

Error bit

Unload bit

Inhibit bit

Found bit

Length value

Position value

Bit 0 of length value

Bit 0 of position value

Back to top

Integer Data File (N7:) Syntax

The following table provides addressing formats and examples to be used when defining CygNet SCADA data groups that are mapped to SLC data files.

Format Parts Description

Nf:e/b

N

Integer file

f

File number

:

Element delimiter

e

Element number

/

Bit delimiter

b

Bit number

N7:2

N7:2/8

N10:36

Element 2, integer file 7

Bit 8 in element 2, integer file 7

Element 36, integer file 10

Back to top

Float Data File (F8:) Syntax

The following table provides addressing formats and examples to be used when defining CygNet SCADA data groups that are mapped to SLC data files.

Format Parts Description

Ff:e

F

Float file

f

File number

:

Element delimiter

e

Element number

F8:2

Element 2, float file 8

Back to top

ASCII Data File Syntax

The following table provides addressing formats and examples to be used when defining CygNet SCADA data groups that are mapped to SLC data files.

Format Parts Description

Af:e

A

ASCII file

f

File number

:

Element delimiter

e

Element number

F9:2

Element 2, ASCII file 9

Back to top

String Data File Syntax

The following table provides addressing formats and examples to be used when defining CygNet SCADA data groups that are mapped to SLC data files.

Format Parts Description

STf:e

ST

String file

f

File number

:

Element delimiter

e

Element number

F9:2

Element 2, string file 9

Back to top

Let us know how we can improve this topic.